Thumbs down Water in Pneumatic lines.

One of our guys discovered water coming out of a thermostat. Checked a few more on that floor and all of them had water. Throw something at me. In need of all the help I can get. This is serious.
  Reply With Quote
Old January 24th, 2009, 10:31 PM   #2
iOperate iOperate is offline
Super Moderator
 
iOperate's Avatar
 
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
iOperate is on a distinguished road
Jonny, this is serious stuff. Could cost you tens of thousands to fix and heads may roll. Is there water in the actuators too? How far has the water gone in relation to where the compressor is?
  Reply With Quote
Old January 24th, 2009, 10:34 PM   #3
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
you might have condensation in your air lines
  Reply With Quote
Old January 24th, 2009, 10:39 PM   #4
TheSuper TheSuper is offline
Administrator
 
TheSuper's Avatar
 
Join Date: Jan 2009
Location: Plano, Texas,
Posts: 95
TheSuper has disabled reputation
Quote:
Originally Posted by Little Jonny View Post
One of our guys discovered water coming out of a thermostat. Checked a few more on that floor and all of them had water. Throw something at me. In need of all the help I can get. This is serious.
Is it manual bleed or auto bleed? Auto blow down cannot be trusted. Is your cooler working? What changed with your system in the last 6-8 months? This should not be happening duing winter.
  Reply With Quote
Old January 26th, 2009, 10:18 AM   #5
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
Check your air drier unit (refrigeration unit), is it functioning well. A working unit does'nt necessarily mean it's working well. Is the bleed solenoid functioning well. How often does the system bleeds? When was the last time the system was checked and found free of water in the lines?
  Reply With Quote
Old January 26th, 2009, 11:36 AM   #6
Colin J Colin J is offline
Junior Member
 
Join Date: Jan 2009
Posts: 6
Colin J is on a distinguished road
In pneumatic system the media (Air) must be dry and oil free. This is why a dryer (refrigeration unit) and Oil seperator are incorperated between the compressor and the tank. I have seen automatic blow down, manual and even a old steam trap installed in the bottom of the tank to drain out the water. The TANK should be blown down each shift, depending on the outside humidity.

Once I found an air line connected from the bottom of a main air supply line, instead of from the top and all the moisture that was in the line drained into this brance causing major problems. If moisture accumilated in the line, the slope of the main line should be away from the branch lines and a drain valve available at the lowest point.

If the main or branch air line goes through a cold area the moisture in the air line could condensate inside the line and cause water problems down stream (branch line).

Check out these Site for Pneumatic Air soultions.

NECC Delivers - johnson controls, hvac training, honeywell thermostat

Air/Oil Separators

Colin J
  Reply With Quote
Old January 26th, 2009, 11:40 AM   #7
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
I agree with Colin.
  Reply With Quote
Old February 16th, 2009, 04:32 PM   #8
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Here's the beef.

When the original air dryer failed, the service provider (Big name in the industry) replaced it with a unit of lesser capacity so it could not effectively dry the air. The unit was recently replaced with a larger unit and monitoring is in progress. Thanks to you all for pitching in. You guys rock.
  Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:48 PM.


Powered by vBulletin® Version 3.8.0
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15