One of our guys discovered water coming out of a thermostat. Checked a few more on that floor and all of them had water. Throw something at me. In need of all the help I can get. This is serious.
|
|
|
|
#2 |
|
Super Moderator
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
![]() |
Jonny, this is serious stuff. Could cost you tens of thousands to fix and heads may roll. Is there water in the actuators too? How far has the water gone in relation to where the compressor is?
|
|
|
|
#3 |
|
Senior Member
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
![]() |
you might have condensation in your air lines
|
|
|
|
#4 | |
|
Administrator
Join Date: Jan 2009
Location: Plano, Texas,
Posts: 94
![]() |
Quote:
|
|
|
|
|
#5 |
|
Member
Join Date: Jan 2009
Posts: 43
![]() |
Check your air drier unit (refrigeration unit), is it functioning well. A working unit does'nt necessarily mean it's working well. Is the bleed solenoid functioning well. How often does the system bleeds? When was the last time the system was checked and found free of water in the lines?
|
|
|
|
#6 |
|
Junior Member
Join Date: Jan 2009
Posts: 6
![]() |
In pneumatic system the media (Air) must be dry and oil free. This is why a dryer (refrigeration unit) and Oil seperator are incorperated between the compressor and the tank. I have seen automatic blow down, manual and even a old steam trap installed in the bottom of the tank to drain out the water. The TANK should be blown down each shift, depending on the outside humidity.
Once I found an air line connected from the bottom of a main air supply line, instead of from the top and all the moisture that was in the line drained into this brance causing major problems. If moisture accumilated in the line, the slope of the main line should be away from the branch lines and a drain valve available at the lowest point. If the main or branch air line goes through a cold area the moisture in the air line could condensate inside the line and cause water problems down stream (branch line). Check out these Site for Pneumatic Air soultions. NECC Delivers - johnson controls, hvac training, honeywell thermostat Air/Oil Separators Colin J |
|
|
|
#7 |
|
Member
Join Date: Jan 2009
Posts: 43
![]() |
I agree with Colin.
|
|
|
|
#8 |
|
Senior Member
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
![]() |
Here's the beef.
When the original air dryer failed, the service provider (Big name in the industry) replaced it with a unit of lesser capacity so it could not effectively dry the air. The unit was recently replaced with a larger unit and monitoring is in progress. Thanks to you all for pitching in. You guys rock. |
|