VFD's blowing fuses

Guys, my brand new VFD driven fans are blowing 50amp fuses over night, almost daily. All the geniuses have looked at it and cant seem to find any problems. Any clues???
  Reply With Quote
Old February 16th, 2009, 04:01 PM   #2
iOperate iOperate is offline
Super Moderator
 
iOperate's Avatar
 
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
iOperate is on a distinguished road
What are these fan supplying? Is there more demand at night vs. day time? Do these fans ever shut down on a typical day?
  Reply With Quote
Old February 16th, 2009, 06:19 PM   #3
TheSuper TheSuper is offline
Administrator
 
TheSuper's Avatar
 
Join Date: Jan 2009
Location: Plano, Texas,
Posts: 94
TheSuper has disabled reputation
Do you know the damper/inlet vane position when the fuse blows?
  Reply With Quote
Old February 16th, 2009, 09:37 PM   #4
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Quote:
Originally Posted by iOperate View Post
What are these fan supplying? Is there more demand at night vs. day time? Do these fans ever shut down on a typical day?
They are fresh air fans. Less demand at night, almost minimal. May be 30%. Yes, they shut down at midnight and start up at 4am.
  Reply With Quote
Old February 17th, 2009, 12:03 AM   #5
Electro Electro is offline
Junior Member
 
Electro's Avatar
 
Join Date: Jan 2009
Location: Peterborough
Posts: 5
Electro is on a distinguished road
Maybe the drives are not properly matched to the motors ?
  Reply With Quote
Old February 17th, 2009, 01:53 PM   #6
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
How many fuses is it blowing?
  Reply With Quote
Old February 17th, 2009, 06:36 PM   #7
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Quote:
Originally Posted by 143 View Post
How many fuses is it blowing?
Just one phase but its never the same.
  Reply With Quote
Old February 17th, 2009, 09:24 PM   #8
Lazy Pup Lazy Pup is offline
Junior Member
 
Join Date: Feb 2009
Location: Calgary, AB.
Gender: Dude
Posts: 21
Lazy Pup is on a distinguished road
Jonny, you need to hook up an analyser to understand the conditions its tripping under. Such as time, voltage, amps drawn etc. Does your automation system track any of this? You say its a VFD so it must be microprocessor controlled. Do you have any fault codes? Come on, cough up some codes and lets see where we can take this.
  Reply With Quote
Old February 17th, 2009, 09:27 PM   #9
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by Lazy Pup View Post
Jonny, you need to hook up an analyser to understand the conditions its tripping under. Such as time, voltage, amps drawn etc. Does your automation system track any of this? You say its a VFD so it must be microprocessor controlled. Do you have any fault codes? Come on, cough up some codes and lets see where we can take this.
I think Lazy Pup is on to something here............................
  Reply With Quote
Old March 3rd, 2009, 05:19 PM   #10
ryanedwards ryanedwards is offline
Junior Member
 
Join Date: Jan 2009
Location: Claremont, Ontario
Gender: Male
Posts: 18
ryanedwards is on a distinguished road
Sounds like you have a voltage problem in the building. This fuse problem is common when your incoming power is not clean and it will drive your mechanics nuts because it is intermittent. You may have voltage spikes or dips that will blow your fuses or trip off your unit, or maybe you have harmonics on the line that your drives don't like. Hook a scope up to your incoming power and be patient. You will have to set it up to sample at intervals as fine as possible as the fluctuations by be short (half second). This means, you may be resetting it often. You may have to do this for quite a while before you can prove that you have an incoming power problem from the grid. I have been through this before, and it can be a very painful process.
  Reply With Quote
Old March 3rd, 2009, 11:35 PM   #11
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
Guys, is it just one fan that is blowing fuses or is it a few of them?
  Reply With Quote
Old March 5th, 2009, 07:33 PM   #12
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Quote:
Originally Posted by 143 View Post
Guys, is it just one fan that is blowing fuses or is it a few of them?
Two identical fans but they are not consistent meaning, very rarely will both fans blow fuses on the same day. They kinda take turns.
__________________
There is nothing new under the sun but there are lots of old things we don't know. - Ambrose Bierce
  Reply With Quote
Old March 6th, 2009, 05:11 AM   #13
iOperate iOperate is offline
Super Moderator
 
iOperate's Avatar
 
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
iOperate is on a distinguished road
Quote:
Originally Posted by ryanedwards View Post
Sounds like you have a voltage problem in the building. This fuse problem is common when your incoming power is not clean and it will drive your mechanics nuts because it is intermittent. You may have voltage spikes or dips that will blow your fuses or trip off your unit, or maybe you have harmonics on the line that your drives don't like. Hook a scope up to your incoming power and be patient. You will have to set it up to sample at intervals as fine as possible as the fluctuations by be short (half second). This means, you may be resetting it often. You may have to do this for quite a while before you can prove that you have an incoming power problem from the grid. I have been through this before, and it can be a very painful process.
I think Ryan is on to something here. If they are tripping during a specific time window (eg: 4am to 6am) then you can safely make an assumption provided they are not tripping on start up. I had a similar problem a while back and it was determined to be a power quality (low voltage) issue.
  Reply With Quote
Old March 17th, 2009, 10:30 AM   #14
ryanedwards ryanedwards is offline
Junior Member
 
Join Date: Jan 2009
Location: Claremont, Ontario
Gender: Male
Posts: 18
ryanedwards is on a distinguished road
Wanted to follow up to see what finally came out of this? Let us know!
  Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 07:32 PM.


Powered by vBulletin® Version 3.8.0
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15