VFD's blowing fuses
Guys, my brand new VFD driven fans are blowing 50amp fuses over night, almost daily. All the geniuses have looked at it and cant seem to find any problems. Any clues???
|
|
|
|
#2 |
|
Super Moderator
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
![]() |
What are these fan supplying? Is there more demand at night vs. day time? Do these fans ever shut down on a typical day?
|
|
|
|
#3 |
|
Administrator
Join Date: Jan 2009
Location: Plano, Texas,
Posts: 94
![]() |
Do you know the damper/inlet vane position when the fuse blows?
|
|
|
|
#4 |
|
Senior Member
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
![]() |
|
|
|
|
#5 |
|
Junior Member
Join Date: Jan 2009
Location: Peterborough
Posts: 5
![]() |
Maybe the drives are not properly matched to the motors ?
|
|
|
|
#6 |
|
Member
Join Date: Jan 2009
Posts: 43
![]() |
How many fuses is it blowing?
|
|
|
|
#7 |
|
Senior Member
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
![]() |
|
|
|
|
#8 |
|
Junior Member
Join Date: Feb 2009
Location: Calgary, AB.
Gender: Dude
Posts: 21
![]() |
Jonny, you need to hook up an analyser to understand the conditions its tripping under. Such as time, voltage, amps drawn etc. Does your automation system track any of this? You say its a VFD so it must be microprocessor controlled. Do you have any fault codes? Come on, cough up some codes and lets see where we can take this.
|
|
|
|
#9 | |
|
Senior Member
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
![]() |
Quote:
|
|
|
|
|
#10 |
|
Junior Member
Join Date: Jan 2009
Location: Claremont, Ontario
Gender: Male
Posts: 18
![]() |
Sounds like you have a voltage problem in the building. This fuse problem is common when your incoming power is not clean and it will drive your mechanics nuts because it is intermittent. You may have voltage spikes or dips that will blow your fuses or trip off your unit, or maybe you have harmonics on the line that your drives don't like. Hook a scope up to your incoming power and be patient. You will have to set it up to sample at intervals as fine as possible as the fluctuations by be short (half second). This means, you may be resetting it often. You may have to do this for quite a while before you can prove that you have an incoming power problem from the grid. I have been through this before, and it can be a very painful process.
|
|
|
|
#11 |
|
Member
Join Date: Jan 2009
Posts: 43
![]() |
Guys, is it just one fan that is blowing fuses or is it a few of them?
|
|
|
|
#12 | |
|
Senior Member
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
![]() |
Quote:
__________________
There is nothing new under the sun but there are lots of old things we don't know. - Ambrose Bierce |
|
|
|
|
#13 | |
|
Super Moderator
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
![]() |
Quote:
|
|
|
|
|
#14 |
|
Junior Member
Join Date: Jan 2009
Location: Claremont, Ontario
Gender: Male
Posts: 18
![]() |
Wanted to follow up to see what finally came out of this? Let us know!
|
|