Old January 26th, 2009, 11:43 AM   #41
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
looks like it narrows down to an overloaded transformer.
  Reply With Quote
Old January 26th, 2009, 11:55 AM   #42
TheSuper TheSuper is offline
Administrator
 
TheSuper's Avatar
 
Join Date: Jan 2009
Location: Plano, Texas,
Posts: 94
TheSuper has disabled reputation
Quote:
Originally Posted by 143 View Post
looks like it narrows down to an overloaded transformer.
Are you saying that because of all the conditions he has mentioned? I know Sparky was going to check out the transformer today. Dont know what he found.
  Reply With Quote
Old January 26th, 2009, 05:43 PM   #43
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
I was by there today and set up the meter............Looks like an
unbalance load............................S
  Reply With Quote
Old January 26th, 2009, 05:45 PM   #44
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Quote:
Originally Posted by sparky View Post
I was by there today and set up the meter............Looks like an
unbalance load............................S
How do you fix somethingy like that?
  Reply With Quote
Old January 26th, 2009, 06:22 PM   #45
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by Little Jonny View Post
How do you fix somethingy like that?

You shift loads between phase's ,until they are closer to being
the same....................................S
  Reply With Quote
Old January 26th, 2009, 07:32 PM   #46
iOperate iOperate is offline
Super Moderator
 
iOperate's Avatar
 
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
iOperate is on a distinguished road
Thanks for dropping by Sparky and at such short notice. Now, was that hot or WAS THAT HOT?
  Reply With Quote
Old January 26th, 2009, 08:04 PM   #47
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
Hey Sparky, you said that it was an unbalanced load problem. What were your readings compared to the wire size?
  Reply With Quote
Old January 26th, 2009, 08:54 PM   #48
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by 143 View Post
Hey Sparky, you said that it was an unbalanced load problem. What were your readings compared to the wire size?

A 45kva is good for 125amps max at 208 volts , you are only allowed
to load it to 80% or 100 amps . When I check the phase's were
70, 45,90.........this was first thing in the morning.

I'm sure when I check the meter it show higher readings later in the
day.
  Reply With Quote
Old January 26th, 2009, 10:42 PM   #49
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
what actually sparked my curiosity was that somewhere along the line someone mentioned that not one but all the lines felt hot at one point........are you saying that all the phases were drawing above 100A at one point?
  Reply With Quote
Old January 27th, 2009, 06:13 AM   #50
TheSuper TheSuper is offline
Administrator
 
TheSuper's Avatar
 
Join Date: Jan 2009
Location: Plano, Texas,
Posts: 94
TheSuper has disabled reputation
Wow, this is the hottest thread just like the transformer.
  Reply With Quote
Old January 27th, 2009, 04:52 PM   #51
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by 143 View Post
what actually sparked my curiosity was that somewhere along the line someone mentioned that not one but all the lines felt hot at one point........are you saying that all the phases were drawing above 100A at one point?

For sure , I was there early in the morning as the day goes on and more
use is put on the transformer , the hotter it will get................S
  Reply With Quote
Old February 7th, 2009, 04:14 PM   #52
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Well after a week of monitoring the transformer , I've found that it is
not only unbalanced but over loaded. I've recomended that he ungrade
to a 75KVA as soon as he can get approval.

Sparky
  Reply With Quote
Old February 7th, 2009, 10:12 PM   #53
143 143 is offline
Member
 
143's Avatar
 
Join Date: Jan 2009
Posts: 43
143 is on a distinguished road
good job Sparky.
  Reply With Quote
Old February 17th, 2009, 09:35 PM   #54
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by 143 View Post
good job Sparky.

Thanks..........
  Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 04:51 PM.


Powered by vBulletin® Version 3.8.0
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15