Infrared Thermal Imaging of Electrical Systems

What is your frequency of thermal scans and what is the proper procedure to follow when doing a scan so nothing is missed? Please share your thoughts and views.
  Reply With Quote
Old February 12th, 2009, 10:45 PM   #2
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Electrician and the scanning guy shows up. Electrician takes off the panel covers and the other guys scans them/takes pic's. This is not the most accurate way to do this. I'll wait till more input comes in and we shall debate the process.
  Reply With Quote
Old February 14th, 2009, 08:46 PM   #3
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by Little Jonny View Post
Electrician and the scanning guy shows up. Electrician takes off the panel covers and the other guys scans them/takes pic's. This is not the most accurate way to do this. I'll wait till more input comes in and we shall debate the process.

The best time to do this type of scan is when the equipment being scaned
is in use..............A thermal scan only works when there is heat present.

  Reply With Quote
Old February 15th, 2009, 05:08 AM   #4
iOperate iOperate is offline
Super Moderator
 
iOperate's Avatar
 
Join Date: Jan 2009
Location: 3rd Rock From The Sun
Gender: Male
Posts: 101
iOperate is on a distinguished road
But not all equipment is in operation or can be operated while scans are conducted. Eg: Auxiliary chiller and/or boiler equipment, cooling tower fans, pumps etc. So, how useful are these scans if we are missing some of the equipment that cannot be operated or run for an adequate time period before being scanned.
  Reply With Quote
Old February 15th, 2009, 05:22 PM   #5
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by iOperate View Post
But not all equipment is in operation or can be operated while scans are conducted. Eg: Auxiliary chiller and/or boiler equipment, cooling tower fans, pumps etc. So, how useful are these scans if we are missing some of the equipment that cannot be operated or run for an adequate time period before being scanned.

In the case of equipment that is not running ,or not operated for an adequate amount of time , an infered scan may not find any faults.

A visual inspection may be your best solution............................
  Reply With Quote
Old February 16th, 2009, 03:50 PM   #6
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Quote:
Originally Posted by sparky View Post
A visual inspection may be your best solution............................
Thats a lot of work for a building like mine with 1.2 million sq feet. How long should equipment run before you can get a reliable scan?
  Reply With Quote
Old February 16th, 2009, 07:56 PM   #7
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by Little Jonny View Post
Thats a lot of work for a building like mine with 1.2 million sq feet. How long should equipment run before you can get a reliable scan?

the best time to scan equipment is when it is at peak use............
  Reply With Quote
Old February 17th, 2009, 06:58 PM   #8
Little Jonny Little Jonny is offline
Senior Member
 
Little Jonny's Avatar
 
Join Date: Jan 2009
Location: Toronto, Canada.
Gender: Male
Posts: 137
Little Jonny is on a distinguished road
Quote:
Originally Posted by sparky View Post
the best time to scan equipment is when it is at peak use............
I understand, but how do you get peak use out of constant start/stop equipment such as compressors, sump pumps, cooling tower fans etc?
__________________
There is nothing new under the sun but there are lots of old things we don't know. - Ambrose Bierce
  Reply With Quote
Old February 17th, 2009, 09:14 PM   #9
Lazy Pup Lazy Pup is offline
Junior Member
 
Join Date: Feb 2009
Location: Calgary, AB.
Gender: Dude
Posts: 21
Lazy Pup is on a distinguished road
Quote:
Originally Posted by Little Jonny View Post
I understand, but how do you get peak use out of constant start/stop equipment such as compressors, sump pumps, cooling tower fans etc?
You can't. They need visual inspection.
  Reply With Quote
Old February 17th, 2009, 09:33 PM   #10
sparky sparky is offline
Senior Member
 
sparky's Avatar
 
Join Date: Jan 2009
Location: toronto
Gender: male
Posts: 123
sparky is on a distinguished road
Quote:
Originally Posted by Lazy Pup View Post
You can't. They need visual inspection.

And if your doing a visual you may want to tighten up all your
connections..........
  Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:52 PM.


Powered by vBulletin® Version 3.8.0
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15